Emerson Exchange 365
Search
User
Site
Search
User
State
Not Answered
Replies
2 replies
Subscribers
5476 subscribers
Views
10738 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Jesse Delanoy
12 Aug 2025 10:06 PM
How to bulk find and replace within phase class action expressions
5 Replies
Tony Whitehouse
12 Aug 2025 6:37 AM
DeltaV OPC UA Server identifiers (NodeId)
1 Reply
Diane Barkin
12 Aug 2025 12:09 AM
SIS License for Small Engineering Firm
0 Replies
laurent maurer
10 Aug 2025 11:58 AM
Deltav Excel Addin in Deltav 15
6 Replies
Jim K
9 Jul 2025 9:04 PM
DeltaV Live Duplicate Displays
0 Replies
<
>
Similar Posts
Is there a way for a picture to move on a value or condition?
Keeping Hydrogen Moving: Secure, Integrated Pipelines for the H₂ Value Chain
Moving test work
Alarm Priority moving
How to identify when HART field value differs from 4-20mA field value?
Share
Not Answered
How to move a value?
How can I move a value of flow totalizer at particular time?
2 Replies
THENNARASU R
17 Mar 2020 9:15 AM
Use TIMER, ACTION or CALC Block
1. Create a Output Parameter "FLOW_STORE"
2. Add TIMER Block and set a specific time
3. Add ACTION Block and write expression like
IF "Timer Output Parameter" THEN
FLOW_STORE := Totalizer value;
END IF
4. once complete, click the "Parse" button. error must be zero then only your expression is fully correct.
gamella
17 Mar 2020 10:08 AM
As "a particular time" do you mean a TOTAL value from the past is required???
If so, you can use a DT block (Dead Time function block). Wiring INTEGRATOR block OUT into DT/IN and setting desired delay X into DT block provides TOTAL value X seconds in the past.
With this you don't have to wait for X time intervals to get a new value. Notice that DT supports download without resetting t's critical values so you don't need to wait for X time after a download to get first "good" value.