Subject: [EE365 DeltaV Forum] RE: TIME_TO_STR: Error when using single CALC block. No error when code is split across two CALC blocks
 
 

So, not more than 2 mins after I posted this I found a solution! :-D

By putting the IF statement before the TIME statement in a single CALC block it works without issue. That said, I have no idea why this is the case. If anyone has any ideas I'd be happy to hear them!

IF '^/TIME.CV' < '^/STOP.CV' OR '^/TIME.CV' >= '^/START.CV' THEN
'^/PARAM1.CV' := "OK";
ELSE
'^/PARAM1.CV' := "NOT OK";
ENDIF;

'^/TIME.CV' := time_to_str("%h", time('$time_format:Local'));