DELTAV RESOLUTION COMPLAINT
DeltaV 13 or 12 bits resolution
DeltaV Batch Reported Parameter Name Set Resolution Issue.
v13 monitor resolution
RDP with 1920x1200 Resolution
Share
RE: DELTAV RESOLUTION COMPLAINT
Greetings sir,
DeltaV Version: 7.3
I currently have issue with delta opening in complete resolution in
1366*768
But it Opens fine in
1024*768
, please how can I go about this.
Thanks
Kind Regards,
Agbita O. Wisdom
PCS Tech.
Mobil Producing Nigeria Unltd.
Qua Iboe Terminal
Mobile: 07031526341
OUR VISION:
To Make A Difference To Customers In A Timely, Innovative And Creative Manner Everyday Using All Available Resources At Our Disposal.
“Every company leverage the strength of its professionals. If a company is great the professionals made it so” ----by Gabriel Fagade.
From:
Agbita, Wisdom O /C
Sent:
Wednesday, October 23, 2019 10:34 AM
To:
[email protected]
Subject:
DELTAV RESOLUTION COMPLAINT
Greetings sir,
I currently have issue with delta opening in complete resolution in
1366*768
But it Opens fine in
1024*768
, please how can I go about this.
Thanks
Kind Regards,
Agbita O. Wisdom
PCS Tech.
Mobil Producing Nigeria Unltd.
Qua Iboe Terminal
Mobile: 07031526341
OUR VISION:
To Make A Difference To Customers In A Timely, Innovative And Creative Manner Everyday Using All Available Resources At Our Disposal.
“Every company leverage the strength of its professionals. If a company is great the professionals made it so” ----by Gabriel Fagade.
1 Reply
Scott Thompson
23 Oct 2019 5:34 PM
DeltaV v7.3 only supports two display resolutions: 1024x768 and 1280x1024.
1366x768 is a widescreen resolution and while still not supported could probably be made to work if you were at DeltaV v8.4.1 or higher.