Windows Server 2008 - Security patches

We have had a windows update destroy our ability to configure fieldbus devices on our Windows Server 2008 machine, DeltaV explorer hangs when we click on I/O.

Our IT dept connected our server to the Internet for security patches and then forgot to disconnect. Many of the updates that were installed have since removed, however these three (The three .dll update files (msxml4.dll)) cannot be uninstalled and are causing serious issues.

can anyone help?

6 Replies

  • Removal of Windows Updates should be done through Windows Control Panel > Add Remove Programs > View Installed Updates and removing the specific Microsoft Updates that are not approved. Removing them this way should roll back the changed dll files that they modified.

    Tested Updates are documented in Knowledgebase Article AK-1300-0005: "Microsoft Released Security Updates for DeltaV Systems"

    After removing the updates I would suggest running a regall which can be done by: Command Prompt > regall /register > reboot after completion

    The regall will help DeltaV reregister its necessary DLLs, some of which could have been modified by the Microsoft Updates.

  • In reply to Tim Alexander:

    Thanks Tim, ill give it a try..
  • Wow. Is all I can say. Your IT department need to understand that control system machines are not like home PC's. I would most certainly be getting some analysis done on this system to make sure that malware has not been introduced at the same time it was connected to the internet.

    Best practices :

    Never connect control systems directly to untrusted networks - This includes business networks that ultimately contain internet connectivity. Always connect using firewalls/Intrusion Detection etc, utilizing DMZ environments - For example, if there is a need (OSIsoft PI data) - However, in my opinion, patching is not a requirement for making any connections like this.

    Download the approved and tested patches using the Emerson KBs - Always check the hash of the downloaded files.

    Burn the patches to CD/DVD - which should be clean. This should be done on using a machine that has all patches and antivirus up to date

    "Sneakernet" them to your systems/machines. Then install. Always remember to restart the machines after patch installation is complete.

    If you want to be more cautious - Use the Emerson B&R (Acronis) and take regular (weekly) image backups - This will allow for quick rollback. But also this allows you to virtualize your machines to re-create your control machine system set up. Ideal for testing any patches. Remember that this really only tests against the operating system and not the controls side - But may give you a warmer feeling before going live with patches. Also very handy for testing more regular antivirus definition updates.

    If you had system restore enabled you may be able to roll back before the updates.

    I know its probably a bit late and you have found out the hard way....

    PS - Here is a Microsoft link to the MS Parser files and the updates.

    support.microsoft.com/.../list-of-microsoft-xml-parser-msxml-versions
  • In reply to DCSNewbie:

    thank you for the advice I will pass the information on :)
  • GaryL.

    I concur with most of the comments shared by other colleagues here, but due to the critical conditions your system might be into right now, I'd advise you to get support from Emerson to recover your environment based on some of our cybersecurity services. Recovering the workstation that was connected to the internet is certainly an important step, but I see several areas of improvement on your system (from a cybersecurity point of view) that we can help you based on said services offering. Revisiting your network segmentation, security policies and some other key areas would certainly be places to start since you may already be running your DeltaV system on an unsupported deployment type which may lead to many other issues. I highly recommend you to reach out to your local Emerson Impact Partner or Field Sales Office for information about our Performance Services to address your concerns.

    Regards,

    Alexandre Peixoto
  • Hi Gary,
    I am the Business Development Manager for Cybersecurity in Europe based out of the UK and am quite often up in the North East. If you require further help or just information feel free to contact me on [email protected]
    Best regards
    Rob