Emerson Exchange 365
Search
User
Site
Search
User
Replies
3 replies
Subscribers
5478 subscribers
Views
16312 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Benji_Kidmose
30 Aug 2024 4:26 PM
DeltaV - Epochalypse
2 Replies
John Rezabek
30 Aug 2024 1:03 PM
Tune up Trellix to have no impact on DeltaV Operate and PHV?
5 Replies
gbilly
27 Aug 2024 6:08 PM
Assigned new DO Isolated VAC & when testing on false in logic at charm still reading present VAC?
0 Replies
TPatterson
26 Aug 2024 7:54 PM
cut-out dimensions of DeltaV touchscreen workstation
0 Replies
TreyB
23 Aug 2024 7:04 PM
Modbus Serial card, Diagnostic Data
0 Replies
<
>
Similar Posts
Fwd: Telnet session with DeltaV Controller
ProPlus 3rd NIC on Windows Domain?
PK Controller Network Gateway on 3rd party NICs
Get Out of the Double IIoT Bind
Referencing and EM Class Module Block Binding
Share
Fwd: Net work binding when using 4 NIC
Hi
In engineering station 4 nic cards are using
1. Deltav Secondary
2.Deltav Primary
3. Reomte Primary For GPS
4.Plant Lan for printer
Then how to give binding order... For these nic cards
3 Replies
JackC
3 Jul 2018 3:22 PM
Bibin,
I don't quite understand your question in terms of binding order. Do you mean when you do a "Rerun" or "Create Proplus" when performing a workstation configuration? I have never had to bind the NIC cards at all.
If doing a "Rerun", put (1) as the DeltaV Primary, (2) as the DeltaV Secondary, then (3)&(4) should be left in the bottom networks.
Andre Dicaire
3 Jul 2018 9:31 PM
In reply to
JackC
:
The Binding Order was a feature in earlier versions of Windows, and is replaced by the Network Priority in windows 10. In a multi Homed computer, with 4 NIC's, the binding order tells a computer which network it should use first to try and connect to a remote server. Part of this is to keep the DeltaV networks as clean of non-DeltaV traffic.
Workstation Configuration allows you to define the DeltaV primary and Secondary network, but this has nothing to do with the NIC Binding order.
The Operator Workstation installation manual or associated KBA will provide details for the version of DeltaV and OS that you are running.
To set the binding order in Windows 7, you can open the Network and Sharing Center and select the Change Adapter Settings. This will list the NIC's on your computer. Select Advanced/ Advanced Settings and this will call up the dialog that shows you the NIC's in their "order" of priority. I believe for your case, you would use the following order:
1 Plant Lan for printer
2 Remote Primary For GPS
3 Deltav Secondary
4 Deltav Primary
Note that DeltaV communications and anything that explicitly calls by IP address will be directed to the NIC for that subnet. What is also important is that this order be respected on all computers that share these networks. If you inverse this say with the Plant Lan and Remote network, this can cause issues especially with DCOM and/or OPC connections. If some computers don't have the Plant LAN connection, but have the Remote, then it is Remote, then DeltaV Secondary and at the bottom DeltaV Primary.
Andre Dicaire
JackC
3 Jul 2018 9:39 PM
In reply to
Andre Dicaire
:
Andre,
Thanks for your clarification. I never had to deal with "Binding Order" and I was thinking of the workstation configuration.