Seeking a recommendation - PCI-E serial card for a Dell PC to connect via RS-232 to a DeltaV Serial port

The site has purchased a gas chromatograph (process analyzer) whose modbus interface runs in a Dell PC. I want to poll their Modbus slave via RS232 from DeltaV Serial port.

The vendor obtained a card from Amazon . . . so far no luck with communication. Anyone have good experience with an aftermarket PC card?

-John

2 Replies

  • I solved Modbus communication issues for new devices using a Modbus master simulator like QmodMaster available on net. In such way, it is possible to find some Modbus protocol details before to connect to DeltaV. A RS232/ RS485 converter could be necessary or not

    I hope it to help

    Ion Paidiu
  • John

    You could easily use the DeltaV Serial Card in RS232 Mode but that will limit 50 feet and special cable is needed.

    Make sure to match the pin out.

    If you have a chromatograph that has OPC server, that also could be an option for integration

    Sent from my iPhone

    Jose Carias | Project Manager II
    Control Southern Inc. | 3850 Lakefield Drive | Suwanee | Georgia | 30024
    T: - | M: 770-243-0619 | F: 770-623-3663
    [email protected]
    Facebook
    LinkedIn
    Twitter
    YouTube
    Products & Services | After Hours Emergency
    Check out our website!
    www.ControlSouthern.com
    ​A Member of the Emerson Local Business Partner Network
    On Jun 7, 2018, at 5:07 PM, John Rezabek <[email protected]> wrote:

    Update from Emerson Exchange 365
    <4TWI5A73YMNM-jpg_2D00_70x70x2-jpg>
    John Rezabek

    The site has purchased a gas chromatograph (process analyzer) whose modbus interface runs in a Dell PC. I want to poll their Modbus slave via RS232 from DeltaV Serial port.

    The vendor obtained a card from Amazon . . . so far no luck with communication. Anyone have good experience with an aftermarket PC card?

    -John

    View online

     

    You received this notification because you subscribed to the forum.  To stop receiving updates from only this thread, go here.

    Flag this post as spam/abuse.