John Stephens
6 May 2021 9:03 PM
Configuration or Tips for developing Operate Graphics with workstations with different resolution displays.
0 Replies
GeloCortez
3 May 2021 7:00 PM
Cascade Control - Level/Flow - Slave Loop fails
7 Replies
KoBriZo
30 Apr 2021 4:17 PM
DeltaV Live "undefined" value DVSYS.Read()
5 Replies
hoang nguyen
27 Apr 2021 9:30 PM
Virtual Controller Communication on a Multinode Simulation
5 Replies
kravindranath
26 Apr 2021 5:44 PM
CIOC Communication failure
1 Reply
<
>
Similar Posts
What is the exact difference between the Unit Parameters and Recipe parameters?
exact installation location of Profibus gateway in order to transmit Hart signals to AMS
What to Do When the DeltaV Calc Block Is Not Enough
What is the named state parameter for ISEL block SELECT_TYPE?
what type of faceplate should be used for a lab entry function block.
Share
Not Answered
What is the exact use of CRACK_TIME in DC Block?
Could someone explain what is the exact use of CRACK_TIME in DC Block?
2 Replies
Matt Stoner
30 May 2017 7:12 PM
Consider a valve with Open and Close limit switches:
If you Open the valve and it is currently close, the crack time is the amount of time given to see the Close limit switch go away (which should be quick, i.e. 1 or 2 seconds)
If the Close limit doesn't go away, the valve is probably not moving or the switch is broken and so the DC fails earlier instead of waiting for the entire Open travel time before failing
manik
30 May 2017 7:23 PM
In reply to
Matt Stoner
:
Hi Matt, Thanks for the response.