Emerson Exchange 365
Search
User
Site
Search
User
State
Not Answered
Replies
2 replies
Subscribers
5482 subscribers
Views
17874 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
ElectroTech
2 Jan 2024 4:28 PM
Single RDP Session To Server 2022 Machines
2 Replies
naira182
14 Dec 2023 8:51 AM
Auto Adjust of Faceplates on DeltaV Live
3 Replies
Invalid String
11 Dec 2023 11:08 PM
DeltaV 13.3.1 | PHV Connecting to the wong data server
0 Replies
ATK
8 Dec 2023 7:22 PM
Regarding Rosemont 2051 Rev 2.1 DD file For DeltaV 10.3
3 Replies
TreyB
30 Nov 2023 8:57 PM
Area Control Network over VPN
13 Replies
<
>
Similar Posts
What is the exact difference between the Unit Parameters and Recipe parameters?
exact installation location of Profibus gateway in order to transmit Hart signals to AMS
What to Do When the DeltaV Calc Block Is Not Enough
What is the named state parameter for ISEL block SELECT_TYPE?
what type of faceplate should be used for a lab entry function block.
Share
Not Answered
What is the exact use of CRACK_TIME in DC Block?
Could someone explain what is the exact use of CRACK_TIME in DC Block?
2 Replies
Matt Stoner
30 May 2017 7:12 PM
Consider a valve with Open and Close limit switches:
If you Open the valve and it is currently close, the crack time is the amount of time given to see the Close limit switch go away (which should be quick, i.e. 1 or 2 seconds)
If the Close limit doesn't go away, the valve is probably not moving or the switch is broken and so the DC fails earlier instead of waiting for the entire Open travel time before failing
manik
30 May 2017 7:23 PM
In reply to
Matt Stoner
:
Hi Matt, Thanks for the response.