Emerson Exchange 365
Search
User
Site
Search
User
State
Not Answered
Replies
2 replies
Subscribers
5482 subscribers
Views
18051 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
imh301
15 Feb 2021 6:15 AM
PK Controller
3 Replies
Summer
12 Feb 2021 11:23 PM
We are considering upgrading our DeltaV system from 14.3.0 to 14.3.1 this year. Just looking for any feedback from anyone who has done this on a physical network. What issues did you run into? What to watch out for? Any Recommendations?
1 Reply
John Rezabek
12 Feb 2021 7:18 PM
ALMGRP_ALM and COMMON_ALM in flood suppression module redundant?
1 Reply
rhamlin
11 Feb 2021 9:09 PM
Watch Area with prepopulated tags
1 Reply
Mohamed Elsaber
10 Feb 2021 4:40 PM
Watch List utility for DeltaV
8 Replies
<
>
Similar Posts
What is the exact difference between the Unit Parameters and Recipe parameters?
exact installation location of Profibus gateway in order to transmit Hart signals to AMS
What to Do When the DeltaV Calc Block Is Not Enough
What is the named state parameter for ISEL block SELECT_TYPE?
what type of faceplate should be used for a lab entry function block.
Share
Not Answered
What is the exact use of CRACK_TIME in DC Block?
Could someone explain what is the exact use of CRACK_TIME in DC Block?
2 Replies
Matt Stoner
30 May 2017 7:12 PM
Consider a valve with Open and Close limit switches:
If you Open the valve and it is currently close, the crack time is the amount of time given to see the Close limit switch go away (which should be quick, i.e. 1 or 2 seconds)
If the Close limit doesn't go away, the valve is probably not moving or the switch is broken and so the DC fails earlier instead of waiting for the entire Open travel time before failing
manik
30 May 2017 7:23 PM
In reply to
Matt Stoner
:
Hi Matt, Thanks for the response.