Emerson Exchange 365
Search
User
Site
Search
User
State
Not Answered
Replies
2 replies
Subscribers
5482 subscribers
Views
17812 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
MarcS
21 Nov 2024 2:13 PM
Export user manager
1 Reply
Todd Jaco
20 Nov 2024 9:20 AM
Best Practices for Implementing Operator Training Systems for DeltaV using Mimic Simulation Software
24 Replies
ATK
17 Nov 2024 6:50 AM
PID output holding during AO failure.
0 Replies
Rishi
14 Nov 2024 8:02 PM
Shared Operator account for windows login and individual operator accounts.
2 Replies
Peter Benedict
25 Oct 2024 11:45 PM
How can I use a fieldbus pressure transmitter 3051 revision 8 dd file (host DeltaV 11.3) to work for DeltaV 9.3.
0 Replies
<
>
Similar Posts
What is the exact difference between the Unit Parameters and Recipe parameters?
exact installation location of Profibus gateway in order to transmit Hart signals to AMS
What to Do When the DeltaV Calc Block Is Not Enough
What is the named state parameter for ISEL block SELECT_TYPE?
what type of faceplate should be used for a lab entry function block.
Share
Not Answered
What is the exact use of CRACK_TIME in DC Block?
Could someone explain what is the exact use of CRACK_TIME in DC Block?
2 Replies
Matt Stoner
30 May 2017 7:12 PM
Consider a valve with Open and Close limit switches:
If you Open the valve and it is currently close, the crack time is the amount of time given to see the Close limit switch go away (which should be quick, i.e. 1 or 2 seconds)
If the Close limit doesn't go away, the valve is probably not moving or the switch is broken and so the DC fails earlier instead of waiting for the entire Open travel time before failing
manik
30 May 2017 7:23 PM
In reply to
Matt Stoner
:
Hi Matt, Thanks for the response.