Check if a Picture Contains a Module in Alarm

Is there any way to check whether a main picture contains any modules in alarm? I want to create an overview picture that shows what pictures have alarms. The pictures do not necessarily correspond to the DeltaV areas (i.e. multiple pictures may have modules from the same area or a single picture may have modules from multiple areas).

Thanks,

Josh

  • Hey there is a way to do this - we call them "alarm groups" and they are separate from the DeltaV areas. But it's rather hard to describe all the details of building the alarm groups and interfacing them with the graphics in a single post. So feel free to email me at [email protected] and I can help get you started.
  • In reply to Chris Harvey:

    Just sent you an email
  • Great question, @kmdcs, this need is currently being evaluated for a possible future enhancement within the DeltaV product as a standard out of the box method of accomplishing your need. In the interim, @ChrisHarvey, can we ask you to please share/describe your solution with the Emerson community?

    Camilo Fadul | DeltaV Solution Marketing Director

    https://www.linkedin.com/in/cfadul

  • In reply to Camilo Fadul:

    We developed an outside application that uses Deltav’s OPC Alarm and Events to assess the alarms from the control modules and generate a grouping mechanism based on the tags in the displays. We then have a mechanism to communicate this information back down the Deltav application thus giving us the ability to show overall alarm grouping for individual displays or other group of tags on the operator’s displays. @cfadul please contact Eric LeBlanc ([email protected]) for more details.
  • Hello,
    Is this an add on application for DeltaV ?

    Regards
    Viswa Pinninti


    Sent from my iPhone
  • Hi Josh,

    We recently implemented a strategy that might be what you're looking for. So to give you a quick overview, picture navigation is done through buttons located on the bottom toolbar
    (I think DeltaV refers to this as the alarm banner). Each button has a picture title and replaces the current picture when clicked. We wanted a quick way to let operators know when they had a module in alarm on any of the pictures. We created a border around each button that becomes visible when a module located on that picture becomes active. It also changes
    color based on alarm priority and flashes when unacknowledged. I'll now get into the coding procedure.

    First, in every class-based module (Analog Inputs, Digital Inputs, Motor Controls, PID, etc.) we dropped a Calc block that runs the following expression:

    IF '^/ALARMS[1].CUALM' != 0 THEN
    'OUT1.CV' := '^/ALARMS[1].PRI' + '^/ALARMS[1].NALM'
    ELSE 'OUT1.CV' := 0
    ENDIF

    This code outputs a numerical value based on the priority level of the alarm (.PRI) and adds 1 if the alarm is unacknowledged by the operator (.NALM = new alarm). Below are our
    standards in place:

    11 = WARNING ( yellow)
    12 = NEW WARNING (flashing yellow)
    13 = URGENT (orange)
    14 = NEW URGENT (flashing orange)
    15 = CRITICAL (red)
    16 = NEW CRITICAL (flashing red)

    We then created a new area that has an equipment module for every picture in the system. Within each equipment module we dropped a Signal Selector function block with SEL_TYPE =
    MAX. Inputs to this block (up to 16) are external references tied to the number described above in every module found on that picture. So this means we had to go to every picture
    and record which modules were dropped on that picture. If there were more than 16 modules on a picture, we had to add 2 more Sig Sel blocks. One to find the max of the remaining
    modules and one to choose the highest value between the two outputs of the Sig Sel blocks. What we end up with is a numerical value telling us the highest priority alarm active on
    that picture. Once you assign the button border visibility and color animations for each button you're all set.

    This does require maintenance over time. As points are either added or removed from the picture you'll have to go back and edit these equipment modules to call for the correct
    modules. I'll admit it's not the easiest solution in the world but it got what we needed done and it works really well. The yellow, orange, and red flashing buttons really grasp an
    operator's attention and it works with our graphics that were built with human centered design (HCD) in mind. If anyone has any recommendations or concerns with this solution I'm
    absolutely open to hearing those.

    -Charles