I want to know how many I/O module could be assigned to a dedicated mx or sx controller?what is the main limitation for that?
This from the Product Data Sheet:
I/O Targeting.
The M-series Zone 2 Remote I/O scanner supports targeting of Classic I/O to controllers on a per card basis. For example, a card can be owned by a controller, with different I/O cards owned by a different controller, with the limit that a Remote I/O scanner can support 4 controllers maximum.
Each DeltaV controller can have up to 16 Remote I/O scanners associated with it.
The DeltaV system supports up to 120 remote I/O scanners. The scanners communicate on the same Ethernet network as the controllers and workstations.
I hope this helps.