Hi Guys,
Does anyone know what would be the parameter paths for browsing the Comm parameter of the DeltaV Zone 2 remote IO nodes & Exist parameter for its cards.
If we look at the the below Snap shot, I was able to browse the Exist parameter of a card for the Remote IO node just like the card of controller. But it gave ***(parameter not configured) error. See below left side.
For the Comm parameter of the Remote IO node I manually entered the path(Not Browsed) just like the one which is available for the controller. But it does not resolve & gives error ***.
I would like to know what is the parameter paths to browse the Comm parameter for PRI & SEC links for a DeltaV Remote IO node & Exist parameter for the cards. I need this to show in graphics just like we have graphics for controllers & its cards.
PS: The browsed overall integrity parameter path for cards of remote IO works just like cards of controllers.
Manzoor
Have you tried Right clicking the parameter in Diagnostics and selecting 'Properties'? This opens a dialog with the appropriate path displayed. Next, try that path in Watchit.exe.
I don't have Remote I/O to test this with, but give it a shot if you haven't already.
In reply to Youssef.El-Bahtimy:
Youssef
I checked the path in watchit as well as in graphics. Attached is the snap for watchit. In graphics I got &&&&.
Does DeltaV Support browsing to its Remote IO node parameters just as for the controllers & DeltaV cards. I hope it does.
Regards
In reply to Manzoor:
After some additional research, I've learned it is unfortunately not possible to reference these parameters, by design. You may submit your request for an enhancement to this design at the User Driven Enhancement Program
http://www.userideas-emerson.com/
There are others requesting this feature, so the more voices the better.
In reply to David Stevenson:
In reply to Lun.Raznik:
Andre Dicaire