DeltaV Remote I/O

Hi.

I want to know how many I/O module could be assigned to a dedicated mx or sx controller?what is the main limitation for that?

3 Replies

  • This from the Product Data Sheet:

    I/O Targeting.

    The M-series Zone 2 Remote I/O scanner supports targeting of Classic I/O to controllers on a per card basis. For example, a card can be owned by a controller, with different I/O cards owned by a different controller, with the limit that a Remote I/O scanner can support 4 controllers maximum.

    Each DeltaV controller can have up to 16 Remote I/O scanners associated with it.

    The DeltaV system supports up to 120 remote I/O scanners. The scanners communicate on the same Ethernet network as the controllers and workstations.

    I hope this helps.

  • Dear Mc_Chow
    Thank you so much. it solved my problem.


  • In reply to J.alizadeh:

    Happy to help. All the best with your DeltaV project.