Similar Posts
DeltaV Reporter issues
DeltaV Xi Reporter issue
DeltaV Batch Reported Parameter Name Set Resolution Issue.
Delta V reporter Issues
DeltaV Reporter vs. SyTech's XL Reporter
Share
Deltav reporter issue
Hi,
I have issue with DeltaV reporter , On April 21.04.2016 23:00 to 22.04.2016 03:00.
when i am taking data for one particular tag value comi
n
g
, but for other it is showing NA.
I have checked all the module and PHV found , value in that is NA.
Please let me know the actual problem and here with atatched screen shot .
--
Regards,
HP
1.png
Thanks,
HP
2 Replies
Steve Linehan
19 May 2016 12:47 PM
This is not a tech support site. Nobody here is paid by Emerson for this. The bulk of people on this site are industy professionals that answer these querys because we like to help people. Please check previous postings to see if your issue has been discussed. The same issue has been cropping up in multiple posts for the last few days.
www.emersonexchange365.com/.../5808
You can always contact Emerson GSC for direct support of your issue.
Youssef.El-Bahtimy
20 May 2016 7:01 PM
It looks as if your historian was shutdown or disconnected from the network during the outage. Both PHV and Reporter state the same thing. Check the event chronicle for records regarding lost connection to the historian during this period.