Emerson Exchange 365
Search
User
Site
Search
User
Replies
1 reply
Subscribers
5479 subscribers
Views
9220 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
MarcS
5 Nov 2021 3:20 PM
Dynamic Reference to an alarm enable
2 Replies
Osw90
4 Nov 2021 7:30 PM
OPC Siemens ----> OPC Delta V 14.3.1
1 Reply
Kenneth Simpton
29 Oct 2021 6:24 AM
Redundancy Alarm on SIS controllersRed
6 Replies
John Rezabek
22 Oct 2021 1:09 PM
Any changes / updates to MPC Pro in recent patches e.g. WS_21 / CTRL_06 (MQ)?
7 Replies
Benji_Kidmose
21 Oct 2021 4:47 PM
.NET Framework on build 1607
6 Replies
<
>
Similar Posts
Creating FrsModules_Theme Dynamos
Module Parameters in Dynamo that generate a skip error, but still work
PCSD Dynamo and the Update Dynamo Expert
Can I edit dynamos in a dynamo set?
Create a module for Diagnostic Parameters
Share
create modules dynamo
hi dears
how can i create a dynamo that can support two modules ?
every module has its data link.
1 Reply
Bill Tinley
30 Oct 2015 11:56 AM
I don't think I have ever done this for a dynamo, but I have done a similar thing for faceplate/detail displays...should work the same way:
It is easy if you can make the name of the second module start with the name of the first module. For example, a pump module (P-100) with an external interlock module (P-100-ILK). Then a single reference for @MOD@ will work for both modules: @MOD@/DC1/SP_D.CV for the pump module, @MOD@-ILK/CND1/OUT.CV for the interlock module, etc.