Emerson Exchange 365
Search
User
Site
Search
User
Replies
1 reply
Subscribers
5478 subscribers
Views
9039 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Rishi
1 Apr 2025 8:04 AM
Best Practices for Thin Client Time Synchronization – Seeking Experiences
0 Replies
GaryL
30 Mar 2025 5:39 PM
VIM 2 and Modbus TCP/IP S-Series Controller
8 Replies
LostEngineer0
7 Mar 2025 4:39 PM
Left mouse click problem
2 Replies
dikshitsh
6 Mar 2025 4:50 PM
Unable to restore Pro plus database from Restore option available in DV database Administration
4 Replies
Kent
5 Mar 2025 1:57 PM
Version 15 FP2 and Rockwell
4 Replies
<
>
Similar Posts
Creating FrsModules_Theme Dynamos
Module Parameters in Dynamo that generate a skip error, but still work
PCSD Dynamo and the Update Dynamo Expert
Can I edit dynamos in a dynamo set?
Create a module for Diagnostic Parameters
Share
create modules dynamo
hi dears
how can i create a dynamo that can support two modules ?
every module has its data link.
1 Reply
Bill Tinley
30 Oct 2015 11:56 AM
I don't think I have ever done this for a dynamo, but I have done a similar thing for faceplate/detail displays...should work the same way:
It is easy if you can make the name of the second module start with the name of the first module. For example, a pump module (P-100) with an external interlock module (P-100-ILK). Then a single reference for @MOD@ will work for both modules: @MOD@/DC1/SP_D.CV for the pump module, @MOD@-ILK/CND1/OUT.CV for the interlock module, etc.