Emerson Exchange 365
Search
User
Site
Search
User
Replies
1 reply
Subscribers
5479 subscribers
Views
9283 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
ATK
24 Apr 2021 12:52 AM
Events View
12 Replies
Senthilkrishnan M
19 Apr 2021 7:23 PM
Abort on Read Error option on CND block
5 Replies
KoBriZo
19 Apr 2021 6:04 PM
Delete an assignment of control module
4 Replies
Shamusk
15 Apr 2021 10:26 AM
Starting the FixBackgroundServer Task as a windows service (IN THE BACKGROUND PROCESSES)
1 Reply
s_brwn
14 Apr 2021 5:24 PM
Process History View- How do I determine what shows up?
1 Reply
<
>
Similar Posts
Creating FrsModules_Theme Dynamos
Module Parameters in Dynamo that generate a skip error, but still work
PCSD Dynamo and the Update Dynamo Expert
Can I edit dynamos in a dynamo set?
Create a module for Diagnostic Parameters
Share
create modules dynamo
hi dears
how can i create a dynamo that can support two modules ?
every module has its data link.
1 Reply
Bill Tinley
30 Oct 2015 11:56 AM
I don't think I have ever done this for a dynamo, but I have done a similar thing for faceplate/detail displays...should work the same way:
It is easy if you can make the name of the second module start with the name of the first module. For example, a pump module (P-100) with an external interlock module (P-100-ILK). Then a single reference for @MOD@ will work for both modules: @MOD@/DC1/SP_D.CV for the pump module, @MOD@-ILK/CND1/OUT.CV for the interlock module, etc.