Emerson Exchange 365
Search
User
Site
Search
User
Replies
1 reply
Subscribers
5479 subscribers
Views
9068 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Benji_Kidmose
30 Aug 2024 4:26 PM
DeltaV - Epochalypse
2 Replies
John Rezabek
30 Aug 2024 1:03 PM
Tune up Trellix to have no impact on DeltaV Operate and PHV?
5 Replies
gbilly
27 Aug 2024 6:08 PM
Assigned new DO Isolated VAC & when testing on false in logic at charm still reading present VAC?
0 Replies
TPatterson
26 Aug 2024 7:54 PM
cut-out dimensions of DeltaV touchscreen workstation
0 Replies
TreyB
23 Aug 2024 7:04 PM
Modbus Serial card, Diagnostic Data
0 Replies
<
>
Similar Posts
Creating FrsModules_Theme Dynamos
Module Parameters in Dynamo that generate a skip error, but still work
PCSD Dynamo and the Update Dynamo Expert
Can I edit dynamos in a dynamo set?
Create a module for Diagnostic Parameters
Share
create modules dynamo
hi dears
how can i create a dynamo that can support two modules ?
every module has its data link.
1 Reply
Bill Tinley
30 Oct 2015 11:56 AM
I don't think I have ever done this for a dynamo, but I have done a similar thing for faceplate/detail displays...should work the same way:
It is easy if you can make the name of the second module start with the name of the first module. For example, a pump module (P-100) with an external interlock module (P-100-ILK). Then a single reference for @MOD@ will work for both modules: @MOD@/DC1/SP_D.CV for the pump module, @MOD@-ILK/CND1/OUT.CV for the interlock module, etc.