Emerson Exchange 365
Search
User
Site
Search
User
Replies
1 reply
Subscribers
5479 subscribers
Views
9062 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
WSoon
2 Oct 2024 3:28 PM
Modbus RTU/RS485
1 Reply
Phil L
27 Sep 2024 6:27 PM
How to relocate an Ether IO device?
0 Replies
s_brwn
25 Sep 2024 12:01 PM
EIOC AWSnt Number of asynchronous buffered writes >10
5 Replies
Weu Butakep
24 Sep 2024 1:24 PM
DeltaV Control Studio File Open Find Feature Anomaly Involving First Sub-unit - Anyone else seeing this?
3 Replies
John Rezabek
20 Sep 2024 1:47 PM
Online Workshops for "Control Loop Foundation" Book (Blevins / Nixon)
2 Replies
<
>
Similar Posts
Creating FrsModules_Theme Dynamos
Module Parameters in Dynamo that generate a skip error, but still work
PCSD Dynamo and the Update Dynamo Expert
Can I edit dynamos in a dynamo set?
Create a module for Diagnostic Parameters
Share
create modules dynamo
hi dears
how can i create a dynamo that can support two modules ?
every module has its data link.
1 Reply
Bill Tinley
30 Oct 2015 11:56 AM
I don't think I have ever done this for a dynamo, but I have done a similar thing for faceplate/detail displays...should work the same way:
It is easy if you can make the name of the second module start with the name of the first module. For example, a pump module (P-100) with an external interlock module (P-100-ILK). Then a single reference for @MOD@ will work for both modules: @MOD@/DC1/SP_D.CV for the pump module, @MOD@-ILK/CND1/OUT.CV for the interlock module, etc.