Momentary push button in DeltaV
How i can implement momentary push button in deltav?
DeltaV
3 Replies
Matt Stoner
14 Aug 2015 5:43 PM
Can you be more specific on where this momentary push button is located (On a display, field button wired to DeltaV, field button not wired to DeltaV, etc) and what function it has (Start Pump, Stop Pump, etc)?
OZ123
15 Aug 2015 6:33 AM
In reply to
Matt Stoner
:
On a display just to start the pump.
GeloCortez
2 Sep 2015 7:57 AM
In reply to
OZ123
:
Hi,
I usually used an INPUT paramater and on delay timer (3-5 seconds) then use an ACTION block to set the INPUT parameter to FALSE again.
INPUT parameter =====> ON DELAY TIMER ======> ACTION BLOCK
then used that input parameter to start the pump (you will have an INPUT parameter TRUE value for 3-5 seconds)