VIM Ethernet Device Configuration Data
Dear All
At Book Online, VIM Ethernet Device Configuration Data just for 2 type of PLC (PLC5 and SLC 505).
Any other type of PLC support VIM?
Thank you all
Best Regard
Arifin Purwanto
1 Reply
DBacker
28 May 2015 1:05 PM
What type of PLC are you using?
You should check the Mynah Technologies website for the VIM manuals. There are at least 2 manuals. Ethernet/IP and Modbus TCP.
For Ethernet/IP they have at least 2 types of communications. One is UCMM Client (I think they also call this Class 3) with DF1 encapsulation to communicate with SLCs and PLC 5 (uses typical Allen-Bradley N, F type register addresses). Control Logix can also do this. There is a separate section in Control Logix for mapping to PLC5 register addreses. Control Logix can also communicate via what is called a Class 1 servier. This can make the VIM look like logix I/O.