Can't clear communication failure alarms from Fieldbus devices that were decommissioned.

I have decommissioned two Fieldbus valves and deleted the associated control module assignments from the node. However I couldn't get rid of the communication alarms from these deleted Fieldbus devcies. Any suggestions on this problem?

  • I'm assuming the alarms were present in the queue before you decommissioned the valves? The easiest way to get rid of these is to re-commission the valves, acknowledge the alarms, and then decommission the devices. In some cases, a total controller download will also clear these alarms from the queue, but I haven't had 100% reliability with this approach.

    If you're not able to re-commission the devices, and a total download doesn't help you, you can create a control module with the same name as your FF device tag, create an alarm in that module named COMM_ALM, assign that module to the controller where the Fieldbus devices were previously commissioned, and clear the COMM_ALM via the control module. I've had good luck with this approach of "tricking" the alarm subsystem.
  • In reply to Ray Emerson:

    You are correct. That's what happened. Thanks a lot for your detailed steps :) Will keep posted.
  • Hi Ray Emerson, the trick of creating a module and deleting it after clearing COMM_ALM worked well.