When a graphic containing an analog value is called up, a message pops up frequently:
LI123/AI1/OUT.F_EGU: Parameter not configured. (Typically a temporary condition).
This message pops up when the graphic is not shown for a long time. The value to be shown is shown correctly.
How can I prevent this message to pop up?
(Version 10.3.1, 12.3.1).
Niklas Flykt
Klinkmann Oy
Key Account Manager safety products
[email protected]
In reply to Niklas Flykt:
In reply to Maarten van der Waal:
In reply to Matt Stoner:
As I remember there is a KBA on guardian about this issue. (Have to check.) The workaround EPM offers is to go to the rectangle animation and remove the 'fetch input range on open' checkbox, save & close the picture. Then open the picture again and check the checkbox again. I've also had the same issue on many level bar indicators and workaround did fix it.
EDIT: Refer to KBA AK-1300-0050 for 2 other workarounds.