Dear All,

I am facing the following problem with the PCSD faceplates

Using Delta V  V11.3.1 and PCD lib version 11C.

Have master slave modules. From Master Module's faceplate I could see the Slave module name. if I click on it, itshould open the Slave module's Faceplate. But it is not opening the slave's one.

The same is happening with Slave module's faceplate as well. i.e from the Slave module's faceplate could not open the master module faceplate by clicking on the Master module's name.

Control Modules are configured properly and downloaded. Funtionality works good from Control Studio.

Kindly share the solution

Thanks,

Manik

 

 

 

8 Replies

  • What is the parameter path specified in the CAS_IN_PATH and SLAVE1 paramters?
     
    Sometimes if you specify a long path, the faceplate can’t resolve which faceplate to open.
     
    From: manik [mailto:[email protected]]
    Sent: Friday, August 29, 2014 2:31 PM
    To: [email protected]
    Subject: [EE365 DeltaV Track] Handshaking between PCSD HCD Faceplate
     

    Dear All,

    I am facing the following problem with the PCSD faceplates

    Using Delta V  V11.3.1 and PCD lib version 11C.

    Have master slave modules. From Master Module's faceplate I could see the Slave module name. if I click on it, itshould open the Slave module's Faceplate. But it is not opening the slave's one.

    The same is happening with Slave module's faceplate as well. i.e from the Slave module's faceplate could not open the master module faceplate by clicking on the Master module's name.

    Control Modules are configured properly and downloaded. Funtionality works good from Control Studio.

    Kindly share the solution

    Thanks,

    Manik

     

     

     

  • In reply to AdrianOffield:

    Length is small.. only 7 letters

  • Just text or with “/” characters?
     
    Which faceplate is the module configured with Loop_FP (default) or something else?
     
    Are you using Zones?
     
     
    From: manik [mailto:[email protected]]
    Sent: Friday, August 29, 2014 3:18 PM
    To: [email protected]
    Subject: RE: [EE365 DeltaV Track] Handshaking between PCSD HCD Faceplate
     

    Length is small.. only 7 letters

  • In reply to AdrianOffield:

    CAS IN PATH with the Module name/OUT

    Slave 1 is only module name

    No Zones

    faceplate is PCSD_Loop_52_FP

  • In reply to manik:

    What is configured for the module faceplate for the module name in Slave 1?

  • Are you getting an error message when trying to open the faceplate(s) - if so what does it say?

  • In reply to Matt Stoner:

    Matt,

    Slave1 I have given the Slave's module name.

    Manik

  • Is the name of slave/master control module correct?

    Have add or remove any frsvariables in the specific PIC ?

    Is it only happening with these two loops ? if it's not

    Just Complie the VBA script for the PCSD_LOOP_52_FP and see if  you are  getting any errors , if there is pl high light & share it with a snap shot