Emerson Exchange 365
Search
User
Site
Search
User
State
Verified Answer
Replies
2 replies
Subscribers
5482 subscribers
Views
11139 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Steven Kang
22 Sep 2021 11:53 AM
VCAT Functionality
1 Reply
s_brwn
20 Sep 2021 12:12 PM
120 VAC DI Isolated Charms not changing state- Always On
7 Replies
SimHogan
15 Sep 2021 4:55 PM
Help diagnosing: mA error seen at the DeltaV AI CHARM
19 Replies
Shamusk
31 Aug 2021 6:00 PM
Sequence (SFC) Programming Standards
7 Replies
CuriousDuncan
27 Aug 2021 11:59 AM
Error while downloading
1 Reply
<
>
Similar Posts
Two System ID in same PLANT LAN and Same proplus name
Connecting two 1420 WirelessHART Gateways on the same fiber backhaul to the DeltaV Primary / Secondary network
Show and write the same parameter for diferent products in display
Delta V Operate support multiple instances of the same faceplate
Can Delta V Operate support multiple instances of the same faceplate?
Share
Answered
Two faceplate is displayed in the same time
Hello,everyone!
I met a problem. I want to display two same faceplate at the same time.for example.dispaly the two Valve's faceplate or two Pump'sfaceplate,But I don't know how to finish it.
All Responses
Answers Only
AdrianOffield
1 Jul 2014 7:11 AM
Inside the usersettings graphics, inside the script (right mouse button on graphic page and -> Edit Script), you will find reference to multiple faceplates (look for a line “frsVariables.GN_IA_LOCKENABLED.CurrentValue = 1” and uncomment it).
That should give you what you want.
From:
Shuyang Liu [mailto:
[email protected]
]
Sent:
Tuesday, July 01, 2014 7:00 AM
To:
[email protected]
Subject:
[EE365 DeltaV Track] Two faceplate is displayed in the same time
Hello,everyone!
I met a problem. I want to display two same faceplate at the same time.for example.dispaly the two Valve's faceplate or two Pump'sfaceplate,But I don't know how to finish it.