Emerson Exchange 365
Search
User
Site
Search
User
State
Verified Answer
Replies
2 replies
Subscribers
5482 subscribers
Views
11093 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Sarah Hart
13 Apr 2023 4:58 PM
DeltaV Modbus Timestamp
4 Replies
hagouda
9 Apr 2023 8:08 AM
dual transmitter to same pid loop
3 Replies
AJARI
5 Apr 2023 2:47 PM
DeltaV SIS
4 Replies
Tom Light
29 Mar 2023 12:06 PM
import/export
8 Replies
Tom Light
27 Mar 2023 6:20 PM
Delta V release dates and support
2 Replies
<
>
Similar Posts
Two System ID in same PLANT LAN and Same proplus name
Connecting two 1420 WirelessHART Gateways on the same fiber backhaul to the DeltaV Primary / Secondary network
Show and write the same parameter for diferent products in display
Delta V Operate support multiple instances of the same faceplate
Can Delta V Operate support multiple instances of the same faceplate?
Share
Answered
Two faceplate is displayed in the same time
Hello,everyone!
I met a problem. I want to display two same faceplate at the same time.for example.dispaly the two Valve's faceplate or two Pump'sfaceplate,But I don't know how to finish it.
All Responses
Answers Only
AdrianOffield
1 Jul 2014 7:11 AM
Inside the usersettings graphics, inside the script (right mouse button on graphic page and -> Edit Script), you will find reference to multiple faceplates (look for a line “frsVariables.GN_IA_LOCKENABLED.CurrentValue = 1” and uncomment it).
That should give you what you want.