· Hi All
I have question...
How to communicate between Siemens s-7 300 to Delta-V Serial Series 2 ??
Dear Marteen Thank you for the respond. For No 1. Yes 2. Yes 3. Yes 4. Yes 5. No 6. from the wiring it should be 4 wire Or full duplex But we tried both way and neither work Half or full duplex
Sent with AquaMail for Android http://www.aqua-mail.com
On May 24, 2014 10:32:59 PM Maarten van der Waal <[email protected]> wrote:
1. Have you enabled the port? 2. Have you configureda device and dataset? 3. Have you configured one to be the master, the other to be the slave? 4. Have you configured the protocol (speed, RTU/ASCII, databits etc) to be the same at both sides? 5. Have you connected the earthing wire on ONLY ONE side? 6. full or half duplex possibility depends on the amount of wires (4 or 2). -----Oorspronkelijk bericht----- Van: arifin [mailto:[email protected]] Verzonden: zaterdag 24 mei 2014 12:40 Aan: [email protected] Onderwerp: RE: [EE365 DeltaV Track] Conecction Siemen s-7 300 to Delta-V Serial Dear Adrian, Thank you for your respond , We already use the CP converter. Another question: Does it support full duplex and half duplex of RS485 ? For the wiring, in which terminal I must put the incoming cable from CP card to DeltaV serial card series 2? I already tried based on books online, but the still cannot communicate. Is there any tips and trick on how we must connect? Please advice. From: AdrianOffield [mailto:[email protected]] Sent: Saturday, May 24, 2014 4:54 PM To: [email protected] Subject: RE: [EE365 DeltaV Track] Conecction Siemen s-7 300 to Delta-V Serial You'll need some form of CP card in the S7-300 chassis, configured for 232/485. ________________________________ From: arifin Sent: 24/05/2014 11:28 To: [email protected] Subject: [EE365 DeltaV Track] Conecction Siemen s-7 300 to Delta-V Serial . Hi All I have question... How to communicate between Siemens s-7 300 to Delta-V Serial Series 2 ??
In reply to arifin:
HI,
- have you crossed the A-B in the other side?
- Do you have the end resistors ON or OFF?
- Have you programmed the initiate block in S7 to configure the port.
- Do you have correct station addresses?
- are you going to use Modbus protocool?
Niklas Flykt
Klinkmann Oy
[email protected]