Profibus DP Siemens s7-300 deltav

The problem I have now is that although achievement set the Profibus DP communicationbetween DCS DeltaV emerson and plc S7-300 either by the integrated dp or the CP342-5, I can not get data from any party Please I need to know how to handle within the S7 andthe DeltaV digital inputs and both analog outputs as they are in the gsd files. in the case ofthe CPU with integrated dp configure Slots accomplishment but do not get data. but in the case of the CP342-5 as a slave as not configure virtual slotfinally here-S7 ConnectionDeltaV apparently is a common question but I have not seen in the support files a sample program for this type of connection if you have one that meets this requirement please do me directions.
PROFIBUS DEVICE SUMMARY - 19:11 Friday, April 11, 2014
Device Name      LO
------ ----      --
Vendor Name      SIEMENS
Model Name       CP 342-5
----- ----       -- -----
Revision         V1.0
 
General
-------
                 Station Non-Existent                                    NO
                 Station Not Ready                                       NO
                 Configuration Fault                                     NO
                 Master Lock                                             NO
                 Parameter Fault                                         NO
                 Invalid Slave Response                                  NO
                 Not Supported                                           NO
                 Extended Diagnostics                                    NO
                 Deactivated                                             NO
                 Sync Mode                                               NO
                 Freeze Mode                                             NO
                 Watchdog On                                             YES           1000ms
                 Slave                                                   YES
                 Static Diagnostics                                      NO
                 Parameterize Request                                    NO
                 Extended Diagnostics Overflow                           NO
                 Device Ident                                            0x80d6
                 Device State                                            Online
                 Master Address                                          1
Device
------
Slot
Signal
------
                 Signal                                 Error
Diagnostic Message Detail
---------- ------- ------
                 Variable                               Value
Diag Msg
---- ---
                 Station Status 1: 0x00
                 Station Status 2: 0x0c
                 Station Status 3: 0x00
                 Device Master Address: 0x01
                 High Byte Of Identifier: 0x80
                 Low Byte Of Identifier: 0xd6
                 No Extended Diagnostic Data
Input
-----
                 
Output
------
                 
Config
------
                 
Param
-----
                 Status Byte To Slave: 0x88
                 Watchdog Factor 1 To Slave: 0x64
                 Watchdog Factor 2 To Slave: 0x01
                 Response Delay Time (tbit) To Slave: 0x0b
                 High Byte ID Value To Slave: 0x80
                 Low Byte ID Value To Slave 0xd6
                 Group ID To Slave 0x00
                 User Parameters:
                 Byte 001 - 003: 0x40  0x00  0x00 

ot configure virtual slotfinally here-S7 ConnectionDeltaV apparently is a common question but I have not seen in the support files a sample program for this type of connection if you have one that meets this requirement please do me directions.

1 Reply

  • Hi,

    Could you give some more data e.g. some screen shots from both sides settings?

    Do you have blinking LED:s bus fault?

    You could recheck the siemens side by reading: support.automation.siemens.com/.../llisapi.dll

    It is really important that you have the lengt of the communication right, there can´t be any differences on either sides.

    also see: www.youtube.com/watch

    Here are some information borrowed from other instances:

    Configuration Parameters

    Slot Configuration

    In DeltaV first 3 slots are to be created for 1st, 2nd and 3rd general ID and are reserved. These 3 slots with no I/O signals are required to be configured in DeltaV for housekeeping purposes. These slots are not configured in the PLC. DeltaV user data slots start at slot 4. PLC user data definition starts from slot 1. The slots assignments for the user data in DeltaV and the PLC must match.

    Tables 3.1 and 3.2 describe the various slot types that can be configured. The slot definition comprises of 3 parts: part 1 defines the direction of data transfer, I stands for Input and Q stands for Output, part 2 defines the slot length and part 3 defines the data format. E.g. Slot definition Master_I Slave_Q 4 B tot lgth means this is Input to Master and Output(Q) from Slave and has 4 Bytes of total length.

    Slot configuration limiting values

    In DeltaV maximum of 32 slots per PLC for user data exchange can be configured starting from Slot 4 to Slot 35. These Slots can be freely mixed. However the same sequence and slot type should be available on the PLC for communication to be established and these are numbered from 1 to 32. Following table lists the maximum data exchange for a PLC over Profibus.

    In the PLC configuration 32 slots can defined for user data exchange and they need to match DeltaV configuration. The Type I stands for Input and Q stands for Output. Output from DeltaV is Input to PLC and vice-versa. While assigning Master Addresses continuous addressing is to be defined for Inputs and Outputs. These addresses are not significant for DeltaV as there are no Address areas in the DeltaV.

    Note : When the CPU of the PLC goes to STOP mode, data in the CPU intermediate memory are overwritten with “0” that is, DeltaV reads its inputs as “0”. However when the Profibus communication stops the CPU intermediate memory is maintained and the CPU uses the stale data. Therefore it is advised to have a life signal in the communication which takes care of this issue.

    Configuration Rules

    The following rules apply:

    1. It is mandatory to ensure the PLC and DeltaV slot configurations are identical (see section 3.1)
    2. Integer and floating point signals held in PLC data blocks must start on an even number byte offset. Values held in byte oriented memory can start on any byte.
    3. It is not necessary to configure all signals in DeltaV.



    Configuring DeltaV

    The following steps are required to configure an instance of a PLC in the DeltaV I/O database:

    1. Select the GSD file corresponding to the S7 hardware model from the Siemens internet site (see section 2.3)
    2. Add the S7 device to the DeltaV Profibus library
    3. Create an instance of a device on a Profibus I/O port
    4. Add slots to the device to match the PLC slot configuration
    5. Add the required signals to the slots.

    Error reporting and recovery

    In case of communication failure the status of the DST is set to BADNOCOM and it can be used in the Control Module for interlocking.

    Recovery of communication with the PLC is automatic.

    there is a document on the E-net : http://www.plctalk.net/qanda/attachment.php?s=282fe718226fa5e7abbf8e2b3a8ae42a&attachmentid=5655&d=1156136099 but you first have to register

    Niklas Flykt 

    Klinkmann Oy

    Key Account Manager safety products

    [email protected]