Hi, I have recently installed a Profibus DP Series 2 card on a system running DeltaV ver.7.3. But during hardware selection, I can only select Series 1. Any advice on this. Thanks

2 Replies

  • I have a customer that was on 7.2 for years, then upgraded to 11.3

     

    In 7.2, explorer only had the choice for Series 1, even though they had Series 2 cards.

     

    On their 11.3 system, the card is still listed as Series 1.  In other words, I don't believe it makes a difference.

     

    Ensure the card is ultimately flashed with the latest firmware (supported for 7.3) before placing in service.

     

    Youssef El-Bahtimy | Systems Integration Technologist
    PROCONEX | 103 Enterprise Drive | Royersford, PA 19468 USA
    Proconex Office: 610 495 2970 | Cell: 267 275 7513


    From: Eddie76 [[email protected]]
    Sent: Thursday, February 06, 2014 12:13 PM
    To: [email protected]
    Subject: [EE365 DeltaV Track] DeltaV Ver.7

    Hi, I have recently installed a Profibus DP Series 2 card on a system running DeltaV ver.7.3. But during hardware selection, I can only select Series 1. Any advice on this. Thanks

  • In reply to Youssef.El-Bahtimy:

    have a look at KBA AP-0700-0106....basically Profibus DP Series 2 card will work fine on DV v7.*