Change of PID Control Action in Runtime

Is there a way of changing a "Reverse Acting" PID loop to "Direct Acting" in runtime?

I tried to write the values for above "16768" and "17792" using calc block but PID block was not happy and did not change the action

Shoaib

4 Replies

  • You have to put the target mode of PID block to Out of Service, then write your value, and then return the PID block to the mode required.

    Regards,

    Matt

  • You first need to take the block Out of Service, switch the action, then return it to the desired mode. 

    Jeff Swennumson 
    PCE Pacific, Inc.

    On Dec 19, 2013, at 6:27 AM, "snizami" <[email protected]> wrote:

    Is there a way of changing a "Reverse Acting" PID loop to "Direct Acting" in runtime?

    I tried to write the values for above "16768" and "17792" using calc block but PID block was not happy and did not change the action

  • Nop, but think about it.
    Process should be one direction for a PID taking control.
    If you need something more complex then you have to implament a more complex control strategyt (maybe two PID and a selection logic)

     
    De: snizami [mailto:[email protected]]
    Enviado: Thursday, December 19, 2013 02:27 PM
    Para: [email protected] <[email protected]>
    Asunto: [EE365 DeltaV Track] Change of PID Control Action in Runtime
     

    Is there a way of changing a "Reverse Acting" PID loop to "Direct Acting" in runtime?

    I tried to write the values for above "16768" and "17792" using calc block but PID block was not happy and did not change the action

  • In reply to gamella:

    See this previous post about Reverse/Direct changing and the way to do this.

    community.emerson.com/.../5250.aspx