I have replaced a charm baseplate with a new one.
But when I mount the DI CHARM on the new baseplate, all the channels (DI 24Vdc low side) becomes active whereas the channels are not wired to the field device (dry contact).
Could you help me to solve this problem?
Best regards
Yoro SIDIBE |
Chef Service
|
Electricité & Régulation
SUCRIVOIRE | UAI Borotou |
BP 100 KORO
M: +225 07 07 21 78
E:
[email protected]
.