DeltaV control studio/faceplate basics
Hello,
Just learning some basics of DeltaV and have a 2 part question:
In a control studio module we are working with a PID  block whose PV_SCALE is ranged from 0 to 36 cc/min. We want to change this range to 0 to 96 cc/min, yet each time we change the range we only seem to modify the 'default' value in the parameters while the 'on line' value remains 0 - 36 cc/min. Why is the change not reflected in the PID block?
Secondly, will the range change be captured on the associated faceplate as well or will I need to modify the faceplate somewhere else?
Any assistance, direction or comments would be greatly appreciated.
Cheers!
  • Make sure to download the control module after you change the values while in configure mode (make sure to check with operations before you download). Once downloaded the change should be refleced in your PID block online and the associated faceplate should update automatically.
  • In reply to tklatt:
    In addition to these forums, there are several other very good resources for building a foundation of your understanding of DeltaV:
    1. Attend the introductory DeltaV courses provided by Emerson and their business partners
    2. Read Books On Line, available on every DeltaV system.
    3. Get familiarity with a DeltaV simulation system before working with a production system.
    Like with any process control system, a fundamental understanding of the architecture and technology is key.
    Good luck!
    Hello and thanks for the information ... I need to clarify a few items:
    The PV_SCALE from the PID block is 0 - 36cc/min and this value is then entered into the OUT_SCALE of a SCLR block.  The OUT of the SCLR block is then entered back into the PID block IN as feedback.
    I have successfully changed PV-SCALES on other modules and seen the changes reflected on the faceplate, but this current module will not let me adjust the PV-SCALE.
    When I am on-line with the module and select the PID block and look at the parameter column I see the on-line value is 0 - 36 cc/min and the default value is 0 - 96 cc/min.  I cannot seem to over-write the 0 - 36 cc/min value.
    Is there something special with the relationship of the PID block and the SCLR blocK?
    Any ideas?
    Cheers!
  • In reply to cwicz77:
    So I have built what you described-
    1. PID/PV_SCALE feeds into SCLR/OUT_SCALE
    2. SCLR/OUT feeds in to PID/IN.
    I have started with a PID/PV_SCALE  of 0-33 whatever, downloaded and can see that as the scale through control studio online.
    I then changed the database value for PID/PV_SCALE to 0-96 whatever, downloaded and can see the updated value on line.
    The only reason I could think for a PID to not accept a changed PV_SCALE is if the PID block is tied to a fieldbus device which is dictating the scale.  Can you confirm whether you are using a fieldbus shadow PID block?
    Can you change the PV_SCALE value online?  You will need to set the PID to OOS mode first, but you should be able to change the scale online for immediate results (again unless it is a fieldbus block).
  • As I understand it, you are making the change offline and then downloading correct?
    Check what references are writing to the PV_SCALE parameter? I would guess that some logic is writing to the parameter preventing the change.  If it is then this might also generate errors as PV_SCALE can only be changed when the PID mode is OOS.
    Check which parameter the FP is pointing to for the EU100 and EU0 fields, some FP’s point to the AI block within a loop module rather than the PID block.
    Sent: Monday, September 23, 2013 9:49 PM
    To: [email protected]
    Subject: [EE365 DeltaV Track] DeltaV control studio/faceplate basics
    Hello,
    Cheers!
  • In reply to AdrianOffield:
    If default range is showing desired value, then it seems the download is done correctly.
    Are you sure some other logic is not writting the PV_SCALE online on the PID block?
    Can you please provide the snapshot of the module online, with property window indicating the PID parameters?
    Amod.
  • First part - assume you downloaded module after change.
    Second part - should not need to modify faceplate as it should reference module using @MOD@ functionality.
    Stuart Greenhalgh
    Phone: 7575385032, Mobile: 7574351909, Fax: 7575385026, E-Mail: [email protected]
    Postal Address: 2301 Wilroy Road, Suffolk, Virginia USA, 23430
    BASF - The Chemical Company
    To:        <[email protected]>
    Date:        09/23/2013 02:48 PM
    Hello,
    Cheers!