Identifying User Sessions in DeltaV Operate and RCS

Can anyone remember the correct path to identify which session is logged into the Remote Client Server (from within DV Operate)?  I have five sessions configured on the RCS, but I need a specific session to default to a different set of graphics, which parameters can I use in usersettings to identify?

Cheers.

  • Hi Adrian

    If the info you mean is the one shown in the toolbar at run mode, have a look to the DataLink of this toolbar.

  • Hello Jack,
     
    Which link on the toolbar, I can’t see a reference to a specific terminal session, only Module/Main/Username.  There is a remote client status icon but that uses the DVSYS.THISUSER/ALARMSRV.CV parameter, it doesn’t tell me I’m using SESSIONX.
     
    What am I missing?
     
    From: Jack_France [mailto:[email protected]]
    Sent: Thursday, August 29, 2013 2:15 PM
    To: [email protected]
    Subject: RE: [EE365 DeltaV Track] Identifying User Sessions in DeltaV Operate and RCS
     

    Hi Adrian

    If the info you mean is the one shown in the toolbar at run mode, have a look to the DataLink of this toolbar.

  • In reply to AdrianOffield:

    Hello Adrian

    You can use DVSYS.THISUSER/TSNAME.A_CV

    Regards,

    Matt

  • Thanks Matt, that was perfect.
     
    Regards,
     
    Adrian
    From: Matt Stoner [mailto:[email protected]]
    Sent: Thursday, August 29, 2013 4:05 PM
    To: [email protected]
    Subject: RE: [EE365 DeltaV Track] Identifying User Sessions in DeltaV Operate and RCS
     

    Hello Adrian

    You can use DVSYS.THISUSER/TSNAME.A_CV

    Regards,

    Matt