Debug View / Force Active Display

Which parameter can be used to generate alarm for debug view active / force active for BPCS modules??

4 Replies

  • Use "MSTATUS[5].CV" or "(MSTATUS & 16) > 0" to get 'Debug View Active' status.

  • In MSTATUS_MASK you can select 'Debug View Active' and/or 'Value Forced'
    active.
    Then when one of these items is seen, the BAD_ACTIVE parameters is set, as
    the MSTATUS is non-zero.

    -----Oorspronkelijk bericht-----
    Van: bobgally [mailto:[email protected]]
    Verzonden: dinsdag 29 januari 2013 05:45
    Aan: [email protected]
    Onderwerp: [EE365 DeltaV Track] Debug View / Force Active Display

    Which parameter can be used to generate alarm for debug view active / force
    active for BPCS modules??

  • In reply to Maarten van der Waal:

    The MSTATUS is an option bit string parameter and you can build an alarm to explicitly set this and view them in an Alarm list in DeltaV.  This is not really an alarm, so I would give it the lowest priority, with Auto Acknowledge.  You'd get an event when the forced value is set and cleared, and a custom Alarm view could show the list of modules with outstanding forces.  

    You'd want to change the default alarm banner/alarm list filter to exclude this priority of alarm.

    Andre Dicaire