Remote Login Graphix Ifix error

Am facing problem when i  remote login my proplus machine (server 2008 delta v 11.3) am not able to open deltav operate .As soon as as i log in i get an error Ifix system not started and error no.2147212799(80042201). Folks any idea about this situation ???

4 Replies

  • Check to make sure DV Operate isn’t already running on the PRO+ (via the local console), remember remote connections on Server 2008 work differently than they did on W2K3, you can connect to the console session as you could in previous versions.
     
    VNC is probably a better alternative than RDP until Emerson finds a solution.
     
     
    From: bobgally [mailto:[email protected]]
    Sent: Sunday, January 20, 2013 2:20 PM
    To: [email protected]
    Subject: [EE365 DeltaV Track] Remote Login Graphix Ifix error
     

    Am facing problem when i  remote login my proplus machine (server 2008 delta v 11.3) am not able to open deltav operate .As soon as as i log in i get an error Ifix system not started and error no.2147212799(80042201). Folks any idea about this situation ???

  • In reply to AdrianOffield:

    i closed workspace in local and tried to connect remotely same error is popping up

  • In reply to bobgally:

    Try "MSTSC /console". Only 1 session is allowed with this.

    Did you install "terminal server role" after or before installing DeltaV? If after, then you may need to re-run workstation configuration.

  • In reply to amodbobade:

    Please refer this problem the Global Service to assistance.  They will be able to help you troubleshoot the issue.