VNC with Pro Plus and App Station

I've been using VNC Server to connect remotely to Pro Plus and Application Station, this generally works fairly well with Mirror Driver (hardware acceleration).  However, I was wondering if it's possible to use Remote Desktop; if I disable flexlock can I use remote desktop?  The reason I ask is, occasionally VNC has glitches (black screen on logins, etc).  I'm running WS2008 now for Pro Plus and App Station.  I was wondering what everyone else uses for this purpose.  Currently we don't run terminal services, everything is a workgroup, and App Station and Pro Plus are on separate computers.  I realize I could purchase a "Pro" license, but I really don't need a 2nd session.

 

 

 

17 Replies

  • I totally agree with Frank that black screens are unacceptable. The client
    is not able to see what the external connection is doing, introducing a big
    security item. Also, remote discussion with the client requires a screen
    which is visible to the client and the remote connection at the same time at
    both sides.
    For 10.3.1 and before I still use PCAnywhere. This was in the list of
    'allowed' programs, but for some reasons disappeared from this list.
    It would be good (to make an understatement) when DeltaV would deliver or
    allow some solution where the desktop of the P+ and AS would be usable and
    visible for both sides (client and remote).

    -----Oorspronkelijk bericht-----
    Van: Frank Seipel [mailto:[email protected]]
    Verzonden: zondag 16 december 2012 17:44
    Aan: [email protected]
    Onderwerp: [EE365 DeltaV Track] VNC with Pro Plus and App Station

    I've been using VNC Server to connect remotely to Pro Plus and Application
    Station, this generally works fairly well with Mirror Driver (hardware
    acceleration). However, I was wondering if it's possible to use Remote
    Desktop; if I disable flexlock can I use remote desktop? The reason I ask
    is, occasionally VNC has glitches (black screen on logins, etc). I'm
    running WS2008 now for Pro Plus and App Station. I was wondering what
    everyone else uses for this purpose. Currently we don't run terminal
    services, everything is a workgroup, and App Station and Pro Plus are on
    separate computers. I realize I could purchase a "Pro" license, but I
    really don't need a 2nd session.







  • In reply to Maarten van der Waal:

    You are following NK-1200-0138 with regards to the VNC server/client installation?  

    I have had to address this issue for several years.  Here are your options:

    1. RealVNC per the article

    2. Buy a TCP/IP KVM (which usually run some flavor of VNC)

    3. Remote client for Pro-plus (which doesn't help you for app stations)

    4. **Custom scripting**

    The **Custom Scripting** solution is one I have developed and use for remote administration of 2008 boxes.  I can provide documentation if you are interested.

  • In reply to Youssef.El-Bahtimy:

    Thanks, I am using the free edition of VNC rather than Enterprise.  The only other difference between KBA, I've always enabled 'Mirror' driver because it makes VNC respond so much faster (more like remote desktop; mirror install is a bit quirky; you connect over VNC, then install & enable it).  I had never read this KBA.  I've read up on this and I believe problem may relate to Mirror driver per kb.realvnc.com/.../I%27m+getting+a+black+screen+when+I+connect+to+VNC+Server but have not yet tried the proposed resolution.  I also found that if I selected one of the other options other than auto when I connect (e.g. 256 or 16 colors) I would not get a black screen.  Black screen would ONLY be on client side.  Oddly it occurs at login, AFTER entering credentials.  Refresh screen does not remedy.  Problem occurs only intermittently.

    Will TCP/IP KVM running VNC, be as fast as VNC with Mirror driver?  It appears these devices are relatively inexpensive, ~$379.40, any ones you recommend?

    I would be interested in #4 Custom Scripting.  Some years ago I had Pc Anywhere.  Does custom script enable remote assistance or something?

    Does Thinsoft's WinConnect Server VS allow login to DeltaV WS2008 console session?  www.thincomputinginc.com/support_winconvs64.aspx

    I also had another question, related to video.  Perhaps this would be better in a separate thread.  When we upgraded to WS2008/DV11.3, Pro Plus no longer supported two monitors... Can I use a USB video adapter,or internal video card to allow me to have two monitors?  Local rep said this wouldn't work a year ago.  It is most useful to see Operate while also running Control Studio or Explorer & I can no longer do this.  Has anything changed on this?

  • In reply to Frank Seipel:

    Regarding which TCP/IP KVM to use, the only Emerson supported models are from Adder:

    http://www.adder.com/emerson

    I believe at least a few of these offer remote console capability.

    The custom solution I wrote basically takes advantage of Terminal services ability to

    1. Send control of a session to the console

    2. Shadow the console session.

    Regarding the Proplus dual screen, I would definitely check back with your local rep...I'm sure they would be happy to update you on any and all changes.  I would also check the 11.3 release notes (AK-1000-0064), as they describe the supported workstation models for a pro-plus and video cards. My impression is that only the T3400, T3500, and R5400 support dual monitors and can be used as Pro-plus.

  • You can also use KVM solutions from Avocent with DeltaV, FYI.

    Aaron

    On Dec 19, 2012, at 8:53 AM, "Youssef.El-Bahtimy" <[email protected]> wrote:

    Regarding which TCP/IP KVM to use, the only Emerson supported models are from Adder:

    http://www.adder.com/emerson

    I believe at least a few of these offer remote console capability.

    The custom solution I wrote basically takes advantage of Terminal services ability to

    1. Send control of a session to the console

    2. Shadow the console session.

    Regarding the Proplus dual screen, I would definitely check back with your local rep...I'm sure they would be happy to update you on any and all changes.  I would also check the 11.3 release notes (AK-1000-0064), as they describe the supported workstation models for a pro-plus and video cards. My impression is that only the T3400, T3500, and R5400 support dual monitors and can be used as Pro-plus.

  • Which Avocent models support remote USB?
     
    We tend to use Adderlink KVM extenders but higher resolutions can be a problem for them.
     
    From: Aaron Crews [mailto:[email protected]]
    Sent: Wednesday, December 19, 2012 8:41 PM
    To: [email protected]
    Subject: Re: [EE365 DeltaV Track] VNC with Pro Plus and App Station
     
    You can also use KVM solutions from Avocent with DeltaV, FYI.

    Aaron

    On Dec 19, 2012, at 8:53 AM, "Youssef.El-Bahtimy" <[email protected]> wrote:

    Regarding which TCP/IP KVM to use, the only Emerson supported models are from Adder:

    http://www.adder.com/emerson

    I believe at least a few of these offer remote console capability.

    The custom solution I wrote basically takes advantage of Terminal services ability to

    1. Send control of a session to the console

    2. Shadow the console session.

    Regarding the Proplus dual screen, I would definitely check back with your local rep...I'm sure they would be happy to update you on any and all changes.  I would also check the 11.3 release notes (AK-1000-0064), as they describe the supported workstation models for a pro-plus and video cards. My impression is that only the T3400, T3500, and R5400 support dual monitors and can be used as Pro-plus.

  • I use the Avocent HMX stuff without any issues. Handles up to 1920x1200x2.

    Aaron

    On Dec 19, 2012, at 9:34 PM, "AdrianOffield" <[email protected]> wrote:

    Which Avocent models support remote USB?
     
    We tend to use Adderlink KVM extenders but higher resolutions can be a problem for them.
     
    From: Aaron Crews [mailto:[email protected]]
    Sent: Wednesday, December 19, 2012 8:41 PM
    To: [email protected]
    Subject: Re: [EE365 DeltaV Track] VNC with Pro Plus and App Station
     
    You can also use KVM solutions from Avocent with DeltaV, FYI.

    Aaron

    On Dec 19, 2012, at 8:53 AM, "Youssef.El-Bahtimy" <[email protected]> wrote:

    Regarding which TCP/IP KVM to use, the only Emerson supported models are from Adder:

    http://www.adder.com/emerson

    I believe at least a few of these offer remote console capability.

    The custom solution I wrote basically takes advantage of Terminal services ability to

    1. Send control of a session to the console

    2. Shadow the console session.

    Regarding the Proplus dual screen, I would definitely check back with your local rep...I'm sure they would be happy to update you on any and all changes.  I would also check the 11.3 release notes (AK-1000-0064), as they describe the supported workstation models for a pro-plus and video cards. My impression is that only the T3400, T3500, and R5400 support dual monitors and can be used as Pro-plus.

  • That is impressive, does it support USB2 remote devices or just local keyboard/mouse devices?
     
    There are a lot of models listed on the site; if I were to consider this as a replacement for an Adderlink KVM Extender, which model would you suggest?
     
    What is the typical retail for these units?
     
    Adrian
     
    From: Aaron Crews [mailto:[email protected]]
    Sent: Thursday, December 20, 2012 6:40 AM
    To: [email protected]
    Subject: Re: [EE365 DeltaV Track] VNC with Pro Plus and App Station
     
    I use the Avocent HMX stuff without any issues. Handles up to 1920x1200x2.

    Aaron

    On Dec 19, 2012, at 9:34 PM, "AdrianOffield" <[email protected]> wrote:
    Which Avocent models support remote USB?
     
    We tend to use Adderlink KVM extenders but higher resolutions can be a problem for them.
     
    From: Aaron Crews [mailto:[email protected]]
    Sent: Wednesday, December 19, 2012 8:41 PM
    To: [email protected]
    Subject: Re: [EE365 DeltaV Track] VNC with Pro Plus and App Station
     
    You can also use KVM solutions from Avocent with DeltaV, FYI.

    Aaron

    On Dec 19, 2012, at 8:53 AM, "Youssef.El-Bahtimy" <[email protected]> wrote:

    Regarding which TCP/IP KVM to use, the only Emerson supported models are from Adder:

    http://www.adder.com/emerson

    I believe at least a few of these offer remote console capability.

    The custom solution I wrote basically takes advantage of Terminal services ability to

    1. Send control of a session to the console

    2. Shadow the console session.

    Regarding the Proplus dual screen, I would definitely check back with your local rep...I'm sure they would be happy to update you on any and all changes.  I would also check the 11.3 release notes (AK-1000-0064), as they describe the supported workstation models for a pro-plus and video cards. My impression is that only the T3400, T3500, and R5400 support dual monitors and can be used as Pro-plus.


  • It looks like it supports USB 2.0 devices other than keyboards and mice. The whole setup gets very powerful (and probably expensive) when you take advantage of the matrix switching (KVM to any station from any station).

    I've never bought them (I have the luxury of testing them out inside Emerson), but since they are an alliance parter (and an Emerson company) your LBP can get you a quote.  It looks like they also sell at places like newegg, etc. 

    Aaron

    On Dec 19, 2012, at 10:10 PM, "AdrianOffield" <[email protected]> wrote:

    That is impressive, does it support USB2 remote devices or just local keyboard/mouse devices?
     
    There are a lot of models listed on the site; if I were to consider this as a replacement for an Adderlink KVM Extender, which model would you suggest?
     
    What is the typical retail for these units?
     
    Adrian
     
    From: Aaron Crews [mailto:[email protected]]
    Sent: Thursday, December 20, 2012 6:40 AM
    To: [email protected]
    Subject: Re: [EE365 DeltaV Track] VNC with Pro Plus and App Station
     
    I use the Avocent HMX stuff without any issues. Handles up to 1920x1200x2.

    Aaron

    On Dec 19, 2012, at 9:34 PM, "AdrianOffield" <[email protected]> wrote:
    Which Avocent models support remote USB?
     
    We tend to use Adderlink KVM extenders but higher resolutions can be a problem for them.
     
    From: Aaron Crews [mailto:[email protected]]
    Sent: Wednesday, December 19, 2012 8:41 PM
    To: [email protected]
    Subject: Re: [EE365 DeltaV Track] VNC with Pro Plus and App Station
     
    You can also use KVM solutions from Avocent with DeltaV, FYI.

    Aaron

    On Dec 19, 2012, at 8:53 AM, "Youssef.El-Bahtimy" <[email protected]> wrote:

    Regarding which TCP/IP KVM to use, the only Emerson supported models are from Adder:

    http://www.adder.com/emerson

    I believe at least a few of these offer remote console capability.

    The custom solution I wrote basically takes advantage of Terminal services ability to

    1. Send control of a session to the console

    2. Shadow the console session.

    Regarding the Proplus dual screen, I would definitely check back with your local rep...I'm sure they would be happy to update you on any and all changes.  I would also check the 11.3 release notes (AK-1000-0064), as they describe the supported workstation models for a pro-plus and video cards. My impression is that only the T3400, T3500, and R5400 support dual monitors and can be used as Pro-plus.

  • Thanks for the info, but have you used point to point KVM’s rather than IP based?
     
    I don’t want to start installing another network just to handle KVM’s.
     
    Adrian
     
    From: Aaron Crews [mailto:[email protected]]
    Sent: Thursday, December 20, 2012 8:37 AM
    To: [email protected]
    Subject: Re: [EE365 DeltaV Track] VNC with Pro Plus and App Station
     
     
    It looks like it supports USB 2.0 devices other than keyboards and mice. The whole setup gets very powerful (and probably expensive) when you take advantage of the matrix switching (KVM to any station from any station).
     
    I've never bought them (I have the luxury of testing them out inside Emerson), but since they are an alliance parter (and an Emerson company) your LBP can get you a quote.  It looks like they also sell at places like newegg, etc. 

    Aaron

    On Dec 19, 2012, at 10:10 PM, "AdrianOffield" <[email protected]> wrote:
    That is impressive, does it support USB2 remote devices or just local keyboard/mouse devices?
     
    There are a lot of models listed on the site; if I were to consider this as a replacement for an Adderlink KVM Extender, which model would you suggest?
     
    What is the typical retail for these units?
     
    Adrian
     
    From: Aaron Crews [mailto:[email protected]]
    Sent: Thursday, December 20, 2012 6:40 AM
    To: [email protected]
    Subject: Re: [EE365 DeltaV Track] VNC with Pro Plus and App Station
     
    I use the Avocent HMX stuff without any issues. Handles up to 1920x1200x2.

    Aaron

    On Dec 19, 2012, at 9:34 PM, "AdrianOffield" <[email protected]> wrote:
    Which Avocent models support remote USB?
     
    We tend to use Adderlink KVM extenders but higher resolutions can be a problem for them.
     
    From: Aaron Crews [mailto:[email protected]]
    Sent: Wednesday, December 19, 2012 8:41 PM
    To: [email protected]
    Subject: Re: [EE365 DeltaV Track] VNC with Pro Plus and App Station
     
    You can also use KVM solutions from Avocent with DeltaV, FYI.

    Aaron

    On Dec 19, 2012, at 8:53 AM, "Youssef.El-Bahtimy" <[email protected]> wrote:

    Regarding which TCP/IP KVM to use, the only Emerson supported models are from Adder:

    http://www.adder.com/emerson

    I believe at least a few of these offer remote console capability.

    The custom solution I wrote basically takes advantage of Terminal services ability to

    1. Send control of a session to the console

    2. Shadow the console session.

    Regarding the Proplus dual screen, I would definitely check back with your local rep...I'm sure they would be happy to update you on any and all changes.  I would also check the 11.3 release notes (AK-1000-0064), as they describe the supported workstation models for a pro-plus and video cards. My impression is that only the T3400, T3500, and R5400 support dual monitors and can be used as Pro-plus.

  • The avocent units can be point to point based using Ethernet cable as the link. They don't need to be in a network. 

    Brian 

    On Dec 20, 2012, at 1:43 AM, "AdrianOffield" <[email protected]> wrote:

    Thanks for the info, but have you used point to point KVM’s rather than IP based?
     
    I don’t want to start installing another network just to handle KVM’s.
     
    Adrian
     
    From: Aaron Crews [mailto:[email protected]]
    Sent: Thursday, December 20, 2012 8:37 AM
    To: [email protected]
    Subject: Re: [EE365 DeltaV Track] VNC with Pro Plus and App Station
     
     
    It looks like it supports USB 2.0 devices other than keyboards and mice. The whole setup gets very powerful (and probably expensive) when you take advantage of the matrix switching (KVM to any station from any station).
     
    I've never bought them (I have the luxury of testing them out inside Emerson), but since they are an alliance parter (and an Emerson company) your LBP can get you a quote.  It looks like they also sell at places like newegg, etc. 

    Aaron

    On Dec 19, 2012, at 10:10 PM, "AdrianOffield" <[email protected]> wrote:
    That is impressive, does it support USB2 remote devices or just local keyboard/mouse devices?
     
    There are a lot of models listed on the site; if I were to consider this as a replacement for an Adderlink KVM Extender, which model would you suggest?
     
    What is the typical retail for these units?
     
    Adrian
     
    From: Aaron Crews [mailto:[email protected]]
    Sent: Thursday, December 20, 2012 6:40 AM
    To: [email protected]
    Subject: Re: [EE365 DeltaV Track] VNC with Pro Plus and App Station
     
    I use the Avocent HMX stuff without any issues. Handles up to 1920x1200x2.

    Aaron

    On Dec 19, 2012, at 9:34 PM, "AdrianOffield" <[email protected]> wrote:
    Which Avocent models support remote USB?
     
    We tend to use Adderlink KVM extenders but higher resolutions can be a problem for them.
     
    From: Aaron Crews [mailto:[email protected]]
    Sent: Wednesday, December 19, 2012 8:41 PM
    To: [email protected]
    Subject: Re: [EE365 DeltaV Track] VNC with Pro Plus and App Station
     
    You can also use KVM solutions from Avocent with DeltaV, FYI.

    Aaron

    On Dec 19, 2012, at 8:53 AM, "Youssef.El-Bahtimy" <[email protected]> wrote:

    Regarding which TCP/IP KVM to use, the only Emerson supported models are from Adder:

    http://www.adder.com/emerson

    I believe at least a few of these offer remote console capability.

    The custom solution I wrote basically takes advantage of Terminal services ability to

    1. Send control of a session to the console

    2. Shadow the console session.

    Regarding the Proplus dual screen, I would definitely check back with your local rep...I'm sure they would be happy to update you on any and all changes.  I would also check the 11.3 release notes (AK-1000-0064), as they describe the supported workstation models for a pro-plus and video cards. My impression is that only the T3400, T3500, and R5400 support dual monitors and can be used as Pro-plus.

  • In reply to Aaron Crews:

    Aaron,

    Do you know if there is a way to disable the USB except for things like mice, keyboards, and speakers?  I am concerned about possibly infecting the workstation with a virus via a flash drive or external hard drive.

    Gareld Butler

  • Gareld,
    Have you considered using group policies to disable USB drives at the computer level?

    Brian

    On Dec 20, 2012, at 7:48 AM, "Gareld Butler" <[email protected]> wrote:

    Aaron,

    Do you know if there is a way to disable the USB except for things like mice, keyboards, and speakers?  I am concerned about possibly infecting the workstation with a virus via a flash drive or external hard drive.

  • In reply to Brian Atkinson:

    On Windows 7/Server 2008 there are group policy objects that do this. But what we have found in testing our v12 application to disable USB ports is that you have to disable the ability for the PC to load any USB drivers at all.  Just blocking USB devices does not catch them all. For example Microsoft does not block a USB from some phones just by disabling USB drives.

  • In reply to Brian Atkinson:

    Brian,

    I have, but really want to keep USB capability at the actual machine as we often use that port when we are doing workstation configuration with a flash drive.  The computer itself is kept in a locked cabinet to maintain security.

    Gareld

    Gareld Butler