DeltaV OPC mirror

i need to read some data from a GE plc.so i connect DeltaV system to the GE PLC using OPC mirror installed in the DeltaV APP station.but i can not see the OPC server of GE plc in the DeltaV system.i have imported the license correctly. could someone give me a hand? or if there is document about DeltaV OPC mirror?

  • Where is the GE OPC server located? You need to point OPC Mirror to the physcial server (PC) where the GE OPC server resides.

  • In reply to AdrianOffield:

    thanks, and how to point OPC mirror to the physcial server? i can see the GE PLC's OPC server using WinCC as a client, but can't using OPC Mirror as both are servers.

  • When you run mirror on the Application station, you configure pipes, both side of the pipe should point to a OPC Server (2 servers total), typically OPC.DeltaV.1 is set as the pipes destination and the GE OPC server is configured as the source.
     
    Mirror is a back-to-back OPC client, it reads form one OPC server and writes to the other.
     
    OPC servers can either be installed locally on the Application station or remotely on other physical servers. To configure mirror for a remote server you configure the host name as the remote PC name (or IP address).
     
    Hope that helps
     
    From: qingshan6013 [mailto:[email protected]]
    Sent: Monday, November 19, 2012 8:53 AM
    To: [email protected]
    Subject: RE: [EE365 DeltaV Track] DeltaV OPC mirror
     

    thanks, and how to point OPC mirror to the physcial server? i can see the GE PLC's OPC server using WinCC as a client, but can't using OPC Mirror as both are servers.

  • In reply to AdrianOffield:

    thanks and i have done what you said, the problem is that i can't browse the GE PLC server in the OPC mirror.the connection between two computers  are good, and the OPCwatchit works well in both physcial when browsing the OPC.DeltaV.1,but can't browse the GE's OPC server in both physical server. if i need to set special settings for the two computers ,like DCOM ?

  • In reply to qingshan6013:

    Can you check if DCOM is enabled and the DCOM security setting?

  • In reply to Joseph Lim:

    thanks, the DCOM has been enabled and i think DCOM security has been setted correctly because i can see the GE OPC server using WINCC as a client.

  • In reply to Joseph Lim:

    Another quention, is the OPCwatchit a general utility tool? if i can use it to browse GE's OPC server in the GE's physical server? thank you.

  • In reply to qingshan6013:

    OPCWatchit can be used to connect and browse other OPC servers, but the browse function is an optional feature and may not be supported on some servers.  

    It's been a long while since I've worked OPC issues, but one thing I'm thinking is that the windows security needs to be set correctly.  The Client needs to be able to authenticate.  Make sure you have a valid user with valid password on both machines.  When you launch OPC Watchit, it is using your windows credentials, and if you are not a valid user, you may not be able to connect to a server.

    For browsing, there is also a need to properly register some OPC Dll's.  Have you run OPC Remote on the GE server?  Maybe some one on this thread can confirm if this would help.  

    Have you tried loging a call with the GSC?  The CTS database likely has this issue documented and you'd get a confirmed solution instead of guesses from "helpful" people like me.  

    Andre Dicaire

  • In reply to Andre Dicaire:

    thank you very much, two control systems have been connected.

  • Was security settings the issue?
     
    From: qingshan6013 [mailto:[email protected]]
    Sent: Thursday, November 22, 2012 8:13 PM
    To: [email protected]
    Subject: RE: [EE365 DeltaV Track] DeltaV OPC mirror
     

    thank you very much, two control systems have been connected.

  • In reply to Joseph Lim:

    i think it was the OPC DLL issue. After i registered these DLL files like opc_aeps.dll,opccomn_ps.dll,opcdaauto.dll...,problem solved.thank you all the same!