SFC Reset Commands

Hi all!

Does the SFC "Reset" command force anything other than redirecting the active step to the initial step? I had assumed that "Reset" would reset the transitions from "True" to "False" but I currently have a sequence that command is set to "Reset" and it still shows transitions to be "True".

Any suggestions on how to ensure the transitions are reset?

Thanks!

2 Replies

  • Transitions will only all show false in Control Studio On-line just after initial download. After that they always show the last evaluated state and only get reset to false when the step above them gets set to active (green box) and the transitions begin being evaluated. This helps with troubleshooting as it always shows the path the logic went through. The SFC Reset command resets a stopped or completed SFC back to the first step, doesn't change any values in the module.