Hello,
I was testing some logic and wanted to be able to simulate switching modes. Instead of implementing the corresponding analog control function block, I just used a parameter of type Mode. I was experimenting with confirming a mode, and wanted to use the "Actual" field, but it is always blank. I've tried using both input and output parameters, and they both have blank "Actual" fields. I read a post about exposing the mode parameter of a Device Control (DC) block as an output and then the "Actual" field is populated. I have not tried that, because I was hoping to just use a parameter. I did try wiring an input parameter to an output parameter, but both parameters still have a blank "Actual" field. Why is the "Actual" field not populating, and/or what is the best method to test Mode.Target versus Mode.Actual?
Thanks.
Here are the numeric values for the modes. These were driven by foundation fieldbus specification and note that IMAN and LO aren't valid Target modes
Mode - Target - ActualOOS - 1 - 1IMAN - n/a - 2LO - n/a - 4MAN - 8 - 8AUTO - 16 - 16CAS - 48 - 32RCAS - 80 - 64ROUT - 144 - 128