The A, B, Cs of Controller Tuning
Forums
Blogs
Library/Resources
Members
Tags
More
Cancel
Create New Post
Comment or Question? Become a member of this Emerson Exchange 365 group. Click here to join.
Gregory K McMillan
12 Jul 2012
Reset Time
tuning
Gain
pid controllers
rate time
Options
Subscribe by email
RSS
More
Cancel
Related
Recommended
Share
The A, B, Cs of Controller Tuning
All of the major tuning methods end up with the same expressions for PID gain, reset time, and rate time when the tuning objective is maximum disturbance rejection. Differences come down to tweaking of the a, b, and c coefficients. Furthermore the use of external-reset feedback (dynamic reset limit), and options such as a setpoint filter, setpoint rate limit, and an enhanced PID for wireless eliminate the need to retune for different objectives.
read more