Terry Blevins and Greg McMillan
3 Oct 2011
"fail open"
Fieldbus
Control
Education
Process Control
Control Design & Commissioning
PID
Final Control Elements
Distributed Control Systems (DCS)
"power failure"
"increase/decrease"
"fail close"
Options
Subscribe by email
RSS
More
Cancel
Related
Recommended
Share
Commissioning Control Systems – Increase/Decrease Selection
The analog output block action on loss of power, that is, fail open or fail closed, is defined in Foundation Fieldbus devices through the configuration of the IO_OPTS parameter. Also, as addressed in Control Loop Foundation – Batch and Continuous Processes...