Entech ToolKit

I have Emerson Entech Toolkit.

I want to use it to help tune some Rockwell PLCs (Compact Logix, SLC500s,...etc)

Is there a way to add Rockwell Controller Types to Entech Tookit?

  • Our EnTech Toolkit collects data via OPC. This data would usually come from the DeltaV or other DCS, but it can also come from a HMI/SCADA with an OPC server interface.
  • Yes. You can add the Rockwell controller. You will need to get the PID algorithm information from your Rockwell documentation so that you can accurately add the new controller. In the Tuner application, go to the main menu and select Setup/Controllers... To create your new controller it is often easiest to select the appropriate Generic controller with the correct PID form - Parallel for example. Right click on the Generic controller and select "New Controller". You will have to create a new Record ID - Something relevant to the controller you are adding. You will also need to set up the "Folder" information so that the new controller is shown correctly in the tree display. Looking at how other controllers are set up will show you how to set up the "Folder" and what other information is needed.