I have a domain system. If I try to log in through the DeltaV station, it will generate such an error in the domain system. (The trust relationship between this workstation and the primary domain failed.) What do you advise to do. Please help. This error occurred after I returned a previously removed copy (acronis true image).

3 Replies

  • Same error, any ideas how to fix this?

    Process Automation Manager

    FERMIC

  • In reply to Jorge L:

    This can be caused by a few things

    1) Time between the DC and the workstation is out
    2) If you have restored the machine from a backup, then the workstation password is likely to be wrong as this is rolled by the domain. In DSA.MSC find the computer object and right click to reset account. Then reboot the workstation. This may fix it.
    3) Log onto the workstation with the local admin, and rejoin it to the domain
  • In reply to Andrew Ingram:

    Great bullets, in my case affected WS is not in domain, still workgroup configuration.