Operator Graphics, Engineering Units not coming through, Isolated to recently built Workstation
Ahoy! All,
We recently made headway with a new build for OPs/ENG  workstation (DV12.3 on Win7_Pro).
Issue we having seems only isolated to this new station.
As per image below, we have noticed that engineering units are not coming through.
Any help will be highly appreciated.
Related post:
emersonexchange365.com/.../engineering-units-not-displaying-in-new-operator-station
CHUZA LONGWE
Control Systems Engineer (Nickel Mine)
DeltaV 12.3.1
longwechuza@gmail.com
  • Update: Re-running the workstation configuration does not resolve the issue. Seems like it may be associated with the below error:
    CHUZA LONGWE
    DeltaV 12.3.1
  • In reply to CHUZA LONGWE:
    Looks like YellowPages is not updating. Can you please send screen capture of C:\DeltaV\bin\YpServiceCtrl.exe, run this on the station that is not working.
  • In reply to Lun.Raznik:
    I run the Auto Update Service Control. Under Enable nothing was ticked. So I ticked them all; Status changed after, I clicked set and then close.
    Re-Downloaded, Op\Eng station, Setup Data, and re-started Station and still no engineering units. Though the other pop-up seems to have come up since the last restart.
    Another thing I have noticed is that every time the station is restarted, it comes up a no configuration status see below (could it be there is configuration file not on the station). And after each restart, a download must be done to overcome this.
    CHUZA LONGWE
    DeltaV 12.3.1
    On RNO-PCS64, kindly check if <DvData>\download\EUDT.SCR contains the unit used in 40320-FIC-3230/AI/OUT_SCALE. If not, ensure the ProPlus have the updated unit, upload and then download setup on ProPlus. Then download setup data for RNO-PCS64. Open Diagnostics (Tools | Auto-Update Diagnostics) to verify EUDT.scr is propagated properly.