Deltav configuration for Windows 10

Does anyone have a document of DeltaV configuration for windows 10? or windows 10 installation manual for deltav?

7 Replies

  • My understanding is that the manual is not nedded anymore as the DeltaV installation will do it for you for Windows 10 and Windows 2016.
  • In reply to Lun.Raznik:

    The only workstation allowed and supported for DeltaV station are the dell station sold by Emerson. Each of these station is delivered with a « recovery DVD » which has to be use to install OS with DeltaV pre-requisite.
  • In reply to LaurentB:

    Thank you for Reply.
    You are right, But there is a problem due to data transfer between workstations, and i want to review windows configuration for deltav, exactly network configuration. I will be grateful for your help.
  • In reply to Valeh :

    In later versions of DeltaV, Windows settings/changes are automated as part of the installation. What version of DeltaV are you using?
  • I found the old XPHelp.chm very helpful to make sure everything was configured correctly in Windows. I haven't looked for what is available on v14 yet.

    Having a guide (at least what are absolutely required settings) could be helpful. This is especially for DeltaV Simulate Standalone which is often installed on a non Emerson supplied workstation.
  • In reply to Lun.Raznik:

    We use of v14, I'm looking for any way to recheck the configuration to ensure.
  • In reply to Valeh :

    I am not aware of any documentation that might help you here. The XPHelp.chm might be a good start but it pales to all the settings that DeltaV applies to workstations:
    - Disable UAC
    - Recommended Windows Firewall configuration (if you are using it)
    - Application of local or domain security policies
    - Hardening of OS/SQL Server/IIS
    - - CIS Benchmarks
    -- IEC 62443* standards

    Your best bet is to contact GSC.