There are 2 identical pelletizing systems in 2 separate DeltaV systems/manufacturing cells.
Different versions - DV7 and DV13.
In DV7 PID performance is satisfactory with gain=0.5, reset=5, PVfilter=10s :
However in DV13 system, where whole project is copied/converted from DV7 system), performance is much worse:
PID tuning is not identical(gain=0.52, reset=10.5, PVfilter=8s) because otherwise pelletizer interlocks because of pressure/flow overshoot.
However, what mystifies me is not performance.
DV7 PID responds to -100 SP change with roughly -2% change to OUT. And DV13 PID has longer reset(so theoretically should be slower), yet responds to same -100 SP change with -5% OUT.
Why 2 PID blocks with the ~identical parameters/scaling/configuration/controlled devices, same PV, same SP change(and therefore error) - return that much different OUT???