I have AMS device manager, as well as DeltaV.
For the most part it works, however I noticed about half of the devices are missing in AMS. I went and attempted to add those devices manually to AMS and noticed the I/O card they should be on is missing. I right-clicked the controller, selected rebuild heiarchy, and they are still missing. Below you can see, im missing I/O card 63, (among others)
Any ideas why I cannot get them in AMS?
In reply to Rune Reppenhagen:
In reply to Eric Bailey:
Wasn’t sure if you were joking, but in case someone who doesn’t know is looking for info, you have to change the channel type from analog to Hart analog. Download the charm or the card if it’s traditional I/o. Right mouse button, auto sense device, let it auto sense. Download again. If it doesn’t find the device it may be because you don’t have the matching device definition, wiring issue, or the field device isn’t HART enabled. We “enable as we go” in the older units. Good luck. I always wonder how we did it before AMS, it has spoiled me for troubleshooting, commissioning, calibrations & just general instrument anything!