Hello All
We are using an adder to calculate our Motor running hours, whenever the motor running hours reach 8192, the adder stops to add.
Attaching the screenshot of Control Studio
Anyone else experienced similar issue while adding incremental values and knows the work around on that?
Thanks in advance
What you are seeing is the rounding error inherent to IEEE-754 floating point number storage (method of storing a floating point number as 32 bits of information). As numbers get larger the resolution of the mantissa decreases. The value of 8192.000485 and 8192 are both stored as 01000110000000000000000000000000 but 2.000485 is stored as 01000000000000000000011111110010. As you can see in the table I've placed below, as the magnitude of the number increases, the accuracy decreases.
As your base number (ADD1/IN2) grows larger you will see differing rounding errors due to the IEEE 754 conversion loosing resolution.
If you want to see the actual results and errors for different values I've found this site useful: https://www.h-schmidt.net/FloatConverter/IEEE754.html