ENABLE HORN FOR ALARM

hI

Our system has two OWS and one EWS. OWS1 sounds audible alarm for every alarm that generates in the banner. The EWS and OWS2 do not but you only see the alarms flash on the banner. What do I change to make the OWS2 sound the horn for every alarm assigned to it. Is this done from the User_Settings.grf?

1 Reply

  • First check that the machine can make any sound at all (speakers plugged in, powered, etc)
    Next check that the Horn is Enabled with the right button on the alarm banner that looks like a Speaker (if there is a red international no symbol then it is disabled)